Commercial Kiln Drying
KDAT
4/8/14
Brent
My company uses a tried and true schedule that cooks KDAT syp @ 135.f/h
In the steps getting to the cook temp, they have the temp ramp set at 10 degrees an hour, with "idle" time when the kiln temp gets to step set-point. it typically takes 14hrs to get to 135.
my question is would it be beneficial to ramp much slower with no "idle" periods, and still get to cooking temp in 14hrs?
quality and cost benefits?
5/9/14       #2: KDAT ...
Gene Wengert-WoodDoc
The ramp is a rather new feature for drying and was introduced by Lignomat with their controls. There was not previous research that showed the benefit of doing this. It was put into the automatic controls so that the boiler was not worked too hard...a key when a marginally sized boiler was heating many kilns.
I have seen many operations using 20 F ramp for KDAT. Unless the specification indicates otherwise, I would use that. During the ramp, the lumber will be at the wet-bulb temperature, so actually WB is more important than DB...the higher the WB (a lot of heating-up cycles keep the vents closed so that they do not lose heat through the vents while heating), the hotter the lumber.
This is for a steam kiln. Things are different with direct-fired, as you have venting all the time due to constantly incoming air from the burner. In this case, the WB is often low, which means you are not heating as fast as you think, so an idle time will allow the lumber to catch up to the DB. I would heat the air much faster again and monitor the WB to know and understand what the lumber is doing. (For example, if you heat to 135 F and the WB is only 110 F, then the lumber only reaches 110 F.)