5000 cfm limit

11/25/14       
Bob Member

I am looking to upgrade our dust collector.
We currently have a Dantherm S-750. Its a bit light for our Rover 30.
I am looking to put the most powerfuly unit I can use indoors. I know that there is a 5000 cfm limit placed on indoor units. Does this mean the unit can not be rated for more than that? Most units are advertized at a almost a free flow CFM. Most units with a load on them will actally be less. Can I put a unit rated at 6000 cfm that actally pulls less?

11/26/14       #2: 5000 cfm limit ...
Dylan Bayliss  Member

Website: http://www.cnc-tool.com

Bob, it all relates to the NFPA 654.
Google it and you will find information related to the Code. It might be worth spending the $42 to buy it as well. The code states the maximum you can put inside is a 5000cfm, open dust system. Different units have a different CFM's at different static pressure. You have to calculate the static pressure of your machine and the duct work and look at the fan curve to determine if the fan will handle the volume of air at the required static load. Your Rover 30 depending on its head configuration has the following requirements as per OEM manual
Air Req:30m/sec (5905fpm) 300mm Port
7634 meters cubed/hour (4493cfm) for Slots A and B
1940 meters cubed/hour (1191cfm) for Slot C
1940 meters cubed/hour (1191 cfm) for Boring operations

I would look at the S-1000
that pulls 5000cfm@7WG with a 400mm inlet, still a little low for OEM requirement but will probably do much better than the s-750 4500cfm@6" with 280mm outlet
We can offer this with dumpster bin $9,500 delivered. Questions, please call
314-504-8098
Dylan Bayliss
www.machineconsult.com

http://www.nederman.com/products/baghouse-dust-collectors/manual-baghouse-dust-collectors/s-series-bag-dust-collectors

12/1/14       #3: 5000 cfm limit ...
Curt Corum

NFPA 664 Standard for the Prevention of Fires and Explosions in Wood Processing and Woodworking Facilities 2012 Edition

12/1/14       #4: 5000 cfm limit ...
Bob

Thanks for your replies.

Is there a way of measuring CFM in the system or do I need to have my duct system calculated to find the resistance?
Would it be feasible to put in a unit capable of pulling more CFM but putting in a damper to limit it so I an get the most out of a system and keep safe legal limit?

12/1/14       #5: 5000 cfm limit ...
Dylan Bayliss  Member

Website: http://www.cnc-tool.com

You can measure the pressure and determine the Air Velocity/cfm based on the Duct size.

http://www.dwyer-inst.com/Product/Pressure/DifferentialPressure/Gages/Ser
iesDM-1000

In response to the last I believe the answer is no. The NFPA 664 is clear on the size of the unit. Most reputable Dust Mfgs that offer inside units will no longer sell you a unit bigger that 5000cfm. If you purchase one the assumed risk is on you and the mfg.
You might be able to use two different units to pull from the same machine, ie connect another 5/7.5hp to the machine to get enough cfm. I am not sure how this would relate to the 664 code and if there is verbiage for or against that.
Dylan

12/1/14       #6: 5000 cfm limit ...
Dylan Bayliss  Member

Website: http://www.machineconsult.com

another option for fpm
http://www.dwyer-inst.com/Product/AirVelocity/Windmeters/MarkIIWSI

then multiply by (88) to get FPM
regards
dylan

12/1/14       #7: 5000 cfm limit ...
Curt Corum

Bob, It is the dust collectors job to overcome the resistance of piping, etc., and pull the total CFM required. In this case, to create a velocity of 5,905 in a 12" diameter duct, the CFM would be 4,600. The resistance must be calculated properly.How many feet of pipe, elbows, flex hose, filter loss, and so forth. Lets say the final requirement is 4,600 CFM at 11.5" SPWG. You would select the dust collector that has those coinciding figures on a performance curve or chart. In case the resistance is a bit less than calculated
and the CFM is higher than necessary, a damper can be installed to purposely induce resistance and lower the CFM delivery. The velocity and coinciding CFM for this machine is much higher than that for typical woodworking machines, but then again, this is not a typical machine. Typical conveying velocities for woodworking dust collection range from 4,000 FPM to 4,500 FPM. It is the CFM in a duct that creates the velocity in feet per minute. There is no guessing as to resistance, it must be derived at accurately. All that I have mentioned pertains to a dust collector dedicated to this machine. NFPA 664, 8.2.2.2.1.6*, Where dampers or gates are used for individual equipment, the volume and velocity resulting from the operation of such dampers or gates shall not reduce the system velocity below the design minimum. Acceptable to use them for the instance I mentioned previously. Another good air flow instrument manufacturer is Alnor.

Curt

12/20/14       #8: 5000 cfm limit ...
cabinetmaker

Bob

I put a 15HP Dustek in just for our Rover on Dylan's advice. The fire dept and the insurance company has looked at it several times and said nothing. We do have it 30 feet from the nearest emergency exit.

I tried a 10hp on it, but the dust shoe is so large that it just could not get enough off the board. The 15hp is night and day. We are going up 12 feet with a 14" main to a 90" and then reduced to a 12" pipe and went straight to the machine with a 12" run elbowed down and hooked on.

We do still have left over chips stuck between the passes, but with return onion skin on the smaller parts its pretty clean.

We are planning on moving it outside this next month and put a VFD or soft start on it.

12/25/14       #9: 5000 cfm limit ...
Factory Owner Member

Bob,

I just recently purchased a building to move my operation into and was faced with the same dilemma.

I looked at large central systems and needing to be able to return the air back into the shop required spark detection as well as abort gates. For a system the size I needed it would have cost around $150k.

What I opted for were 2 20 hp cyclone units rated at 5000 cfm and an existing 10 hp cyclone. They are used in 3 different zones within my operation and this set up with good bag house after filters and cyclones was a fraction of the price.

I know that NFPA 664 is supposed to eliminate the possibility of dust explosions within the dust collectors, but honestly, in shops that have had good housekeeping procedures in place, in my 35 yrs. of woodworking I cannot recall one.

The ones we read and hear about are in grain mills and the like, not in architectural woodworking shops.


Post a Response
  • Notify me of responses to this thread
  • Subscribe to email updates on this Forum
  • To receive email notification of additions to this forum thread,
    enter your name and email address, and then click the
    "Keep Me Posted" button below.

    Please Note: If you have posted a message or response,
    do not submit this request ... you are already signed up
    to receive notification!

    Your Name:
    E-Mail Address:
    Enter the correct numbers into the field below:
     

    Date of your Birth:



    Return to top of page

    Buy & Sell Exchanges | Forums | Galleries | Site Map

    FORUM GUIDELINES: Please review the guidelines below before posting at WOODWEB's Interactive Message Boards (return to top)

  • WOODWEB is a professional industrial woodworking site. Hobbyist and homeowner woodworking questions are inappropriate.
  • Messages should be kept reasonably short and on topic, relating to the focus of the forum. Responses should relate to the original question.
  • A valid email return address must be included with each message.
  • Advertising is inappropriate. The only exceptions are the Classified Ads Exchange, Machinery Exchange, Lumber Exchange, and Job Opportunities and Services Exchange. When posting listings in these areas, review the posting instructions carefully.
  • Subject lines may be edited for length and clarity.
  • "Cross posting" is not permitted. Choose the best forum for your question, and post your question at one forum only.
  • Messages requesting private responses will be removed - Forums are designed to provide information and assistance for all of our visitors. Private response requests are appropriate at WOODWEB's Exchanges and Job Opportunities and Services.
  • Messages that accuse businesses or individuals of alleged negative actions or behavior are inappropriate since WOODWEB is unable to verify or substantiate the claims.
  • Posts with the intent of soliciting answers to surveys are not appropriate. Contact WOODWEB for more information on initiating a survey.
  • Excessive forum participation by an individual upsets the balance of a healthy forum atmosphere. Individuals who excessively post responses containing marginal content will be considered repeat forum abusers.
  • Responses that initiate or support inappropriate and off-topic discussion of general politics detract from the professional woodworking focus of WOODWEB, and will be removed.
  • Participants are encouraged to use their real name when posting. Intentionally using another persons name is prohibited, and posts of this nature will be removed at WOODWEB's discretion.
  • Comments, questions, or criticisms regarding Forum policies should be directed to WOODWEB's Systems Administrator
    (return to top).

    Carefully review your message before clicking on the "Send Message" button - you will not be able to revise the message once it has been sent.

    You will be notified of responses to the message(s) you posted via email. Be sure to enter your email address correctly.

    WOODWEB's forums are a highly regarded resource for professional woodworkers. Messages and responses that are crafted in a professional and civil manner strengthen this resource. Messages that do not reflect a professional tone reduce the value of our forums.

    Messages are inappropriate when their content: is deemed libelous in nature or is based on rumor, fails to meet basic standards of decorum, contains blatant advertising or inappropriate emphasis on self promotion (return to top).

    Libel:   Posts which defame an individual or organization, or employ a tone which can be viewed as malicious in nature. Words, pictures, or cartoons which expose a person or organization to public hatred, shame, disgrace, or ridicule, or induce an ill opinion of a person or organization, are libelous.

    Improper Decorum:   Posts which are profane, inciting, disrespectful or uncivil in tone, or maliciously worded. This also includes the venting of unsubstantiated opinions. Such messages do little to illuminate a given topic, and often have the opposite effect. Constructive criticism is acceptable (return to top).

    Advertising:   The purpose of WOODWEB Forums is to provide answers, not an advertising venue. Companies participating in a Forum discussion should provide specific answers to posted questions. WOODWEB suggests that businesses include an appropriately crafted signature in order to identify their company. A well meaning post that seems to be on-topic but contains a product reference may do your business more harm than good in the Forum environment. Forum users may perceive your references to specific products as unsolicited advertising (spam) and consciously avoid your web site or services. A well-crafted signature is an appropriate way to advertise your services that will not offend potential customers. Signatures should be limited to 4-6 lines, and may contain information that identifies the type of business you're in, your URL and email address (return to top).

    Repeated Forum Abuse: Forum participants who repeatedly fail to follow WOODWEB's Forum Guidelines may encounter difficulty when attempting to post messages.

    There are often situations when the original message asks for opinions: "What is the best widget for my type of shop?". To a certain extent, the person posting the message is responsible for including specific questions within the message. An open ended question (like the one above) invites responses that may read as sales pitches. WOODWEB suggests that companies responding to such a question provide detailed and substantive replies rather than responses that read as a one-sided product promotion. It has been WOODWEB's experience that substantive responses are held in higher regard by our readers (return to top).

    The staff of WOODWEB assume no responsibility for the accuracy, content, or outcome of any posting transmitted at WOODWEB's Message Boards. Participants should undertake the use of machinery, materials and methods discussed at WOODWEB's Message Boards after considerate evaluation, and at their own risk. WOODWEB reserves the right to delete any messages it deems inappropriate. (return to top)


  • Forum Posting Help
    Your Name The name you enter in this field will be the name that appears with your post or response (return to form).
    Your Website Personal or business website links must point to the author's website. Inappropriate links will be removed without notice, and at WOODWEB's sole discretion. WOODWEB reserves the right to delete any messages with links it deems inappropriate. (return to form)
    E-Mail Address Your e-mail address will not be publicly viewable. Forum participants will be able to contact you using a contact link (included with your post) that is substituted for your actual address. You must include a valid email address in this field. (return to form)
    Subject Subject may be edited for length and clarity. Subject lines should provide an indication of the content of your post. (return to form)
    Thread Related Link and Image Guidelines Thread Related Links posted at WOODWEB's Forums and Exchanges should point to locations that provide supporting information for the topic being discussed in the current message thread. The purpose of WOODWEB Forums is to provide answers, not to serve as an advertising venue. A Thread Related Link that directs visitors to an area with inappropriate content will be removed. WOODWEB reserves the right to delete any messages with links or images it deems inappropriate. (return to form)
    Thread Related File Uploads Thread Related Files posted at WOODWEB's Forums and Exchanges should provide supporting information for the topic being discussed in the current message thread. Video Files: acceptable video formats are: .MOV .AVI .WMV .MPEG .MPG .MP4 (Image Upload Tips)   If you encounter any difficulty when uploading video files, E-mail WOODWEB for assistance. The purpose of WOODWEB Forums is to provide answers, not to serve as an advertising venue. A Thread Related File that contains inappropriate content will be removed, and uploaded files that are not directly related to the message thread will be removed. WOODWEB reserves the right to delete any messages with links, files, or images it deems inappropriate. (return to form)